Master BMS ID keeps resetting from 0 to 1 – is this normal?
Quote from RiCCo59163 on September 10, 2026, 2:24 pmI have 4 BMS configured with IDs 0 to 3.
- ID 0 = Master
- ID 1 to 3 = Slaves
When I try to set the Master ID to 0, it automatically changes back to 1 every time.
I’m using the latest firmware version.
Is this normal behaviour?
Apart from this issue, all BMS are working correctly.
Thanks in advance for your help!
Best regards,
I have 4 BMS configured with IDs 0 to 3.
- ID 0 = Master
- ID 1 to 3 = Slaves
When I try to set the Master ID to 0, it automatically changes back to 1 every time.
I’m using the latest firmware version.
Is this normal behaviour?
Apart from this issue, all BMS are working correctly.
Thanks in advance for your help!
Best regards,
Uploaded files:- You need to login to have access to uploads.
Quote from ScanLabs on September 11, 2026, 4:42 amBug Fixed,
please try the attached beta-binaries and let me know.
Now JK-ID can “really” range from 0 to 15.When confirmed I will add fix on next 3.6.4
Manually upgrade from the “UPGRADE” tab.
ScanLabs
Bug Fixed,
please try the attached beta-binaries and let me know.
Now JK-ID can “really” range from 0 to 15.
When confirmed I will add fix on next 3.6.4
Manually upgrade from the “UPGRADE” tab.
ScanLabs
Uploaded files:- You need to login to have access to uploads.
Quote from RiCCo59163 on September 11, 2026, 11:59 amThank you very much, ScanLabs!
I installed the SolarEnergyECUMulti.JK-3.6.3-FIX_01 firmware and can confirm that the fix works perfectly.
My battery system consists of 4 JK-BMS units connected in parallel, configured as 1 Master and 3 Slaves.
With the new FIX_01 firmware, I can now correctly set the Master BMS ID to 0. The setting is saved properly and, most importantly, the Master ID remains at 0 after rebooting the ESP.
Everything is now working correctly with my 4-BMS setup.
Thank you for the very quick response, the fix, and the excellent support! 👍
RiCCo59163
Thank you very much, ScanLabs!
I installed the SolarEnergyECUMulti.JK-3.6.3-FIX_01 firmware and can confirm that the fix works perfectly.
My battery system consists of 4 JK-BMS units connected in parallel, configured as 1 Master and 3 Slaves.
With the new FIX_01 firmware, I can now correctly set the Master BMS ID to 0. The setting is saved properly and, most importantly, the Master ID remains at 0 after rebooting the ESP.
Everything is now working correctly with my 4-BMS setup.
Thank you for the very quick response, the fix, and the excellent support! 👍
RiCCo59163
Uploaded files:- You need to login to have access to uploads.
Quote from ScanLabs on September 11, 2026, 12:38 pmI do suggest you use protocol 001 – is better expecially with shor BMS polling time like yours.
In addition you have info about Cell resistance which are not available with prot 000When you do, be sure to change on the BMS via JK APP or JK-BMS-MONITOR and after on the dongle.
Protocol 001 and the SSBdE dongle, also grant you to use JK-BMS-MONITOR via internet for advance configuration of your BMS .
ScanLabs
I do suggest you use protocol 001 – is better expecially with shor BMS polling time like yours.
In addition you have info about Cell resistance which are not available with prot 000
When you do, be sure to change on the BMS via JK APP or JK-BMS-MONITOR and after on the dongle.
Protocol 001 and the SSBdE dongle, also grant you to use JK-BMS-MONITOR via internet for advance configuration of your BMS .
ScanLabs